Your system is reporting that zone 1 is labeled garage door, but it is programmed as a temperature zone type. It shows up on our end as a 24 hour aux alarm.
Whenever I open the door to exit it chimes with a flood/freeze chime.
If locally you are experiencing the panel reacting as though the door is an evironmental chime, that isn’t an issue mapping from the SEM to Alarm.com, that means the sensor is indeed programmed as a temperature zone on the panel.
We have a programming guide for sensors linked below. In this case it looks like this sensor should be an entry exit zone type, which would be zone type 1. Currently it reports being Zone type 8.