Happy to help with some of these, but there are issues with others. There is a lot of non-standard programming, I would recommend changes.
Zones 28-30 are updated as Glass Break.
Zones 32-34 are updated as Water type.
Zone 39 is updated as a Contact.
Zone 96 is updated as a Non-Burglary medical panic (I believe this is what you intend, correct?)
The problem zones:
Zones 24-26 are programmed as Day Zones (Zone type 5). Glass breaks should generally be either perimeter contacts (Zone type 3, which your other three glass breaks use) or interior follower (Zone type 4).
Day Zone types will only ever show as contacts, as those are the only type of sensors expected for that programming.
Based on your description I would expect Zones 43-46 to be Non-Response sensors, used only for notification purposes in Alarm.com. According to programming though they are set as alarm zones which I do not recommend.
Zone 44 is programmed as a Day zone. This would mean based on your description that Power Loss while armed would result in a potential police burglary response. Zone Type 23 should be used here in conjunction with Alarm.com notifications.
Zone 43 and 45 are programmed as Zone type 8, Aux alarm, used for temperature, medical, and water zones. Zone Type 23 should be used here in conjunction with Alarm.com notifications.
There is no Zone 27, and there is no Zone 46.