Doing some troubleshooting this morning. I’m looking at the z-wave menu/devices. There’s one called ‘PC Controller’(node 1, ID: unknown, manufacturer: unknown)
Is that the 2gig control panel itself? When I select that device it takes a minute then comes back and says it cannot retrieve device settings.
The reason I’m troubleshooting is because after adding an image sensor (ADC-IS-200), my front door shows as open all the time. That triggers an alert for that then after 10 minutes an alert for the t-stat. I have the t-stat set to change settings upon leaving the door open for 10 minutes, so that one is normal.
So I need to figure out why adding the image sensor makes stuff go crazy. I have it uninstalled from the panel at the moment.
Zwave would have nothing to do with the sensor signals, they use a different radio.
I see the door as reporting open currently. Is that the case or is it still not reporting correctly? Can you check and make sure that when adding the IS the first time you didn’t accidentally alter the loop of the door sensor?
Commonly when a sensor does not report close after opening it indicates a loop issue.
If you are on site, can you double check to make sure the door sensor was not physically affected in any way. (magnet isn’t loose/gap is less than half inch, etc.)
I’m looking at the z-wave menu/devices. There’s one called ‘PC Controller'(node 1, ID: unknown, manufacturer: unknown
Do you have a wireless siren? The controller is for the zwave devices. The “unknown” manufacturer/ID for the zwave PC Controller means nothing.
... the door is reporting open again. It’s currently on loop 2...
Verify the programming for the door and IS.
I can tell you right now though, that if it is a DW20R (recessed) and you have it programmed as loop2, then it is programmed improperly. It should be loop1
The window contacts are loop2
The PIR Image Sensor is loop1
A surface contact (e.g., DW10), using the wire leads for a wired switch or sensor (e.g., overhead garage door reed switch) will also be loop1
Another thing to keep in mind when you add new zones is that if you delete a zone and add another where that one previously was, or move zone devices the descriptors will get messed up on alarm.com and with CS. So try not to program a new zone device where a previous zone device existed.
For example, say zone 12 is front door, and zone 9 is motion detector.
You remove zone 12, and add a new IS, and then delete zone 9, and add the front door as zone 13.
Now its all jacked up. Every time motion activates, it will give a notification for “front door open”.
Figured I’d take a look inside. I don’t think I have the same unit as you riven. Here’s a shot of mine from the inside. Also, when I took the cover off it reported a low battery. That must be what the problem is.