How to pair 2GIG-SDS1-345

how do I pair 2GIG-SDS1-345 properly pls, and how long would it take for the certificate to reflect this?

Programming for the ring on a GC3 would be as follows:

System Settings -> Installer Code -> Installer Toolbox -> System Configuration -> Wireless Zones

Zone type: (9) 24 Hour Fire or (16) Fire with Verification (verification requires a full 30 seconds activation or twice within two minutes)
Equipment Code: Existing Smoke
Serial #: (learn in sensor)
Equipment age: New
Loop: 1
Descriptor: INSERT NAME HERE
Reports and Supervision: Enabled

As soon as the sensor is visible in Alarm.com, the Insurance Certificate will reflect the change.