I have a PC1832 with 4 wire smoke detectors, there is a RRS-MOD and a ELOR-1 on the last head. The RRS-MOD is wired in and PGM1 is set to 01 and PGM2 is set to 03. The smoke detector will trigger the alarm panel, all of the smoke detectors will sound. I cancel the alarm on the panel and the alarm silences but the heads will continue to sound. I press the reset button but it has no effect. I have to physically disconnect the RRS-MOD module to get the heads to stop sounding. I do have the 5.6K ohm resisted between AUX+ and PGM1.
Any ideas how to get the smoke detectors to reset from the panel?
Red and yellow are going to AUX+
Black is going to AUX -
Purple is going to PGM1
Orange is going to PGM2
White goes to the smokes on the black wire
Brown goes to the smokes on the red wire
What are the attributes set for the PGM1? They must be set to On, On, Off.
Based on the manual, I don’t see anything wrong with the wiring and setup that you have described. It’s a bit of a head scratcher, unless the RRS-MOD is malfunctioning.
Is that resistor between Aux and PGM1 one that was included with the RRS-MOD? If it came from another source, is it at least 1/4 watt?