I relinked a sensor to the panel to test that more in depth and I monitored it on the panel using the following sections:
- panel settings -> other z-wave devices -> current temperature for sensor
- panel settings -> z-wave device status -> sensor view -> history and events for sensor
Here is what I recorded after pairing the sensor to the panel:
- 9:45AM
73.9 in panel but no event
Nothing in ADC - 74 after forced refresh
- 9:58AM
72.9 in panel with event corresponding event
Still 74 in ADC - 73 after forced refresh.
- 10:01AM
Moved sensor to cooler room
- 10:06
71.8 in panel - no event
- 10:12
70.6 in panel - no event
- 10:20AM
68.6 in panel - corresponding event at 10:18AM
Still 73 in ADC - 70 after refresh
In other words the sensor does properly update the temperature and the panel is aware of it except not all events are recorded for some reason.
The issue seems to be between the panel and ADC has the temperature is not kept in sync in ADC. The refresh only happens if I forced it through the app or, as I mentioned in my first post, once every hour.