Btw, when power is removed from the hardwire, the Qolsys IQ Panel 2 NEVER says it’s offline or anything. It’s almost as if there no STATE being MONITORED in NEAR REAL-TIME. I read in an earlier thread that the HEARTBEAT/CHECK-IN can be up to 75 minutes? If so, let’s see if the status changes in the morning.
I was expecting that unplugging the hardwire translator would have generated a tamper/loss of supervision or some other signalling in near real-time — that part bothers me and indicates this might be a bug in the software?
Ah, no you would not have a real time update when power cycling the Hardwire 16, only if the Hardwire 16 sends a signal, and the Hardwire 16 translator zone is just used for battery supervision. That zone is not indicative of the hardwire sensor zones.
Unplugging and leaving the translator powered down would indeed result in a supervision error at the supervision interval, but not right away.
If there isn’t a separate issue and you’re experiencing a supervision error the only time you should be able to clear that question mark would be relearning the Hardwire 16 into the panel, or rebooting the panel. You might be able to clear it by removing the tamper jumper temporarily. However, the supervision fault would likely then return after the supervision interval, based on what you are describing.
Power cycling the Hardwire 16 is recommended by Qolsys, but is not intended to see an immediate change. If it had a positive impact the zone status would clear at the next supervision interval.
Sensors do not update the panel unless there is a change in status or during a supervision interval.
Ultimately, to clarify everything, the issue that is occurring is that the tamper/battery supervisory zone of the translator is not sending a heartbeat signal, but the other zones are.
So, to verify because I don’t see it above, if you remove and relearn that translator zone, do you see the zone act normally for a time and then revert to unknown status?
Keep in mind since the Translator zone is not technically functional other than battery supervision, that zone should be fine to actually leave out of panel programming, optionally.