I have the Qolsys IQ4 345 version. I have successfully enrolled the FF345 and can cause a tamper alert. When I test the smoke detector nothing is reported by the panel. The sensor is setup on Loop 1 as a smoke detector. What do I have wrong in the setup?
Do you have the new round version of the Firefighter or do you have the older rectangular one? Older units used Loop 2 if I recall correctly.
Also, how long are you activating the smoke detector sounder? It will need to be 8-10 seconds for a good test. Let it run through a couple sets of the siren.